Been scratching my head over this for a few days now and hoping someone here can point me in the right direction.
Running a Victron MultiPlus-II 12/3000 in my motorhome, paired with two Fogstar Drift 200Ah LiFePO4 batteries (so 400Ah total at 12V). When I'm on hookup — specifically plugging into a standard 13A BS1363 socket at a CL site — the socket's fuse or the site's breaker trips intermittently.
I've set the shore power input current limit on the MultiPlus to 10A via VictronConnect, which should theoretically keep things well within the 13A limit. The batteries are sitting at around 40% SOC when this happens, so the charger is working reasonably hard, but still — 10A input limit ought to be respected.
A few specifics that might be relevant:
- MultiPlus AC-in absorption current limit: set to 10A
- Site supply: fairly long cable run to a weatherproof outdoor socket, possibly introducing some voltage drop
- Loads running simultaneously: a small 240V fan heater on low (~750W)
My suspicion is that the inrush current or a brief power factor issue is causing nuisance tripping before the MultiPlus can throttle back, but I genuinely don't know if that's accurate or if I'm barking up the wrong tree.
Has anyone experienced similar issues with CL hookups specifically? Would dropping the input limit to 8A give the system enough headroom, or is the issue more likely on the site's end — dodgy wiring, undersized cable, that sort of thing?