Been down a similar rabbit hole recently for the garden office setup, so this caught my eye.
Running a single MP-II 48/5000 on L1 in a 3-phase property is doable, but there are a few things worth stress-testing before you commit:
Phase imbalance — your DNO might have opinions if you're export-enabled. Worth a quick call to confirm their stance before your G98/G99 paperwork goes in.
ESS assistant behaviour on 3-phase — Victron's own docs note that with only one phase covered, the system won't compensate loads on L2/L3. If your heavy hitters (cooker, EV charger, heat pump) sit on those phases, your self-consumption figures will look disappointing vs. what Click&Design spits out.
CT clamp placement — are you measuring the whole incomer or just L1? Easy to get this wrong and end up with the ESS chasing its tail.
My own experience: I modelled the garden office on VRM's simulator before buying anything, and the real-world figures came within about 8% of the estimate once I'd corrected my shading inputs. The tool is decent but it doesn't account for phase topology at all — you have to think that bit through yourself.
What does your load profile look like across the three phases? That's probably the single biggest variable here. If most of your daytime consumption is naturally on L1 already, a single inverter makes a lot more sense than if you're spread evenly.
Anyone else running a single Multiplus on one leg of a 3-phase grid here? Curious whether others have hit DNO pushback.