Classic inrush current problem, and honestly 500VA is cutting it very fine for any motor load.
Motors typically draw 6–8x their rated running current at startup — so your 220W (roughly 1A running at 240V) quarter-horse could be pulling 6–8A for that half-second kick. That's potentially 1,440–1,920W of instantaneous demand against a 500VA inverter. No wonder it's collapsing the output.
A few things worth checking before you go bigger:
- What's the inverter's surge rating? Most budget units will quote 2x continuous for a few seconds, but motor loads can exceed even that briefly. Check the spec sheet carefully — some cheap inverters are very optimistic about their surge figures.
- Battery condition and internal resistance — even a healthy 24V battery bank can sag badly under sudden inrush if the cells are unbalanced or connections aren't solid. Worth checking individual cell voltages under load with something like a Victron BMV or similar.
- Cable gauge and run length — voltage drop compounds everything here.
My own experience: I had a similar issue running a small pump on a Victron Phoenix 375VA. Moved to a 1200VA unit and the problem vanished entirely. Inverters are generally one area where you don't want to be right at the limit of your rating — I'd suggest sizing at roughly 3x the motor's running wattage as a practical rule of thumb for inductive loads.
Anyone else run motors successfully on smaller inverters with a soft-starter fitted? Curious whether that's a viable route here rather than replacing the whole inverter.