Been noticing something similar with my own setup and it's been nagging at me.
Running a Victron SmartSolar MPPT 100/30 with a pair of AGM batteries (around 200Ah total) on the shepherd's hut, and during spring/autumn when the sun isn't exactly blazing, absorption phase sometimes cuts out embarrassingly quickly — we're talking 5-10 minutes some days.
The thing is, Victron's adaptive absorption algorithm calculates absorption time based on how long bulk took. Short bulk = short absorption. Makes sense in theory, but if your panels barely had enough grunt to push through bulk properly, you can end up with a battery that looks full but really isn't.
A few things worth checking if you're seeing the same:
- What voltage are you actually hitting at the end of bulk? If you're not quite reaching absorption voltage before the transition, something's off
- Are your absorption/float voltages set correctly for your specific AGM? Generic presets in Victron aren't always spot-on — worth checking your battery manufacturer's spec sheet
- Panel sizing vs battery capacity — 160W into 136Ah is a reasonable ratio, but on a dull UK day you're not getting 160W
I ended up manually setting a minimum absorption time of around 2 hours in VictronConnect, which made a noticeable difference to how the batteries were actually holding charge.
Anyone else found the adaptive algorithm a bit too clever for its own good on smaller systems? Curious whether tweaking to a fixed absorption time is the better approach for AGMs generally.