Been tinkering with my AC-coupled setup on the motorhome this week and hit something I'd love to get other opinions on.
Running a Multiplus 2 with a grid-tie inverter AC-coupled on the output, with the PV Inverter Assistant active. The frequency shift mechanism works well enough — once the batteries hit a certain state of charge, the Multi starts walking the frequency up to throttle back the PV inverter. Standard stuff.
What I'm less clear on is where exactly the voltage threshold sits that triggers the frequency shift to begin. I know you can adjust the frequency steps and the upper limit within the assistant settings in VEConfigure, but I'm struggling to find a clean way to set the voltage at which the whole process kicks off. At the moment it seems to start earlier than I'd like, meaning I'm losing usable solar harvest before the batteries are genuinely full.
My bank is 280Ah of Fogstar Drift LiFePO4, so I'm working with a fairly tight absorption window. The difference between "nearly full" and "full" in voltage terms is only a few hundred millivolts, and the assistant seems a bit blunt at that resolution.
Has anyone managed to fine-tune this beyond what the assistant wizard exposes directly? I've seen references to adjusting the "AC voltage setpoint" offset on the output side as a workaround — curious whether anyone's actually used that approach or whether it's more trouble than it's worth.
Also wondering if ESS behaves differently here compared to the standalone PV Inverter Assistant — though I appreciate ESS on a pure off-grid system is a different conversation entirely.