AGM battery problem

by Salty Socket · 1 week ago 20 views 4 replies
Salty Socket
Salty Socket
Member
5 posts
Joined Feb 2025
1 week ago
#21281

Been running a similar parallel AGM setup on my static caravan for a couple of years now, so this caught my attention.

Two Victron AGM 110Ah batteries in parallel is a solid foundation, but I've learned the hard way that parallel AGM banks are surprisingly fussy about how you charge them. A few things worth checking:

Equalisation of charge current — are your cables from each battery to the busbar genuinely the same length and cross-section? Even a small resistance imbalance means one battery works harder than the other. Over months this creates a mismatch you can't easily recover from.

The 25A Victron charger — depending on which profile you've got selected, it might be undersized for a 220Ah effective bank. Victron generally recommend around 10–20% of capacity for AGM, so ideally you'd want 22–44A minimum. At 25A you're at the very bottom of that window, meaning bulk stage takes ages and the batteries may never fully saturate, especially in winter.

Mixed charging sources — if you're combining a solar controller (sounds like a Sunwind unit?) with the mains charger simultaneously, you need to make sure both are configured to the same absorption voltage. Conflicting charge voltages confuse AGM batteries badly and accelerate sulphation.

What symptoms are you actually seeing — low capacity, slow charging, voltage dropping under load? That would help narrow it down considerably. I went through two sets of decent AGMs before I sorted my charge regime properly, so definitely worth diagnosing before throwing money at replacements.

Anyone else on here running parallel AGM banks long-term? Curious whether others have found Victron's Smart Battery Sense made a meaningful difference with temperature compensation.

Borders OffGrid
Borders OffGrid
Active Member
25 posts
thumb_up 5 likes
Joined Jun 2024
1 week ago
#21301

@SaltySocket the post got cut off mid-sentence there — classic AGM behaviour, just dies right when you need it most 😄

Seriously though, what's the actual problem you're seeing? Voltage imbalance between the two? One dragging the other down? Premature sulphation?

I've got a similar parallel AGM setup as emergency

EcoFlow_Gal
EcoFlow_Gal
Active Member
20 posts
thumb_up 1 likes
Joined Mar 2024
1 week ago
#21344

@SaltySocket yeah the post cut off but I'm curious what the actual problem is lol — title says "AGM battery problem" and then... nothing 😅

What's happening with them? Voltage sag under load? Not holding charge? Because with AGMs in parallel you've got a few classic failure modes:

  • one battery dragging the other down
  • uneven ageing (even a few months difference matters)
  • undercharging if your absorb voltage isn't high enough — Victron usually wants around 14.7V for AGMs

My cabin setup ran AGMs for ages before I switched, and uneven parallel banks were honestly the bane of my existence. Worth checking each battery's resting voltage individually before assuming it's a system issue.

Rob Thompson
Rob Thompson
Member
6 posts
Joined Jan 2025
1 week ago
#21366

@SaltySocket yeah the suspense is killing me 😄 in the meantime — two parallel AGMs, are you keeping an eye on the individual battery voltages? Had a similar setup in my shepherd's hut before I switched to lithium and one battery was quietly dragging the other down for months before I realised.

Worth sticking a cheap battery monitor on each one separately rather than just reading the combined bank voltage. Victron SmartShunt is ideal but even a basic one helps spot a weak cell early.

Anyway — finish the post! 👀

LiFePO4Nerd
LiFePO4Nerd
Senior Member
118 posts
thumb_up 80 likes
Joined Apr 2023
1 week ago
#21402

While we wait for @SaltySocket to finish that cliffhanger 😄, @RobThompson raises the most important point here.

Parallel AGMs are deceptively tricky. The batteries never age at exactly the same rate, so over time one starts carrying more of the load. Classic symptom is one running noticeably warmer than the other during charge cycles — that's the one slowly dying while the other looks fine on a basic voltage check.

Worth grabbing a proper battery analyser (the Victron BMV-712 is brilliant for this) and checking internal resistance on each unit individually. Voltage alone tells you almost nothing on AGMs.

Also — how old are these batteries? AGMs on a static caravan often sulfate faster than people expect if they're sitting at partial state of charge over winter. That's usually where the story ends badly.