Right, I'm at my wits' end with this. My MultiPlus 12/3000/120 keeps throwing a low battery alarm and cutting out about 3-4 minutes into a wash cycle. I've got 400Ah of lithium (Winston cells, 4S configuration) sitting at around 80% SOC when it happens, so it's not like the batteries are gasping. The inverter's pulling around 1,800W during the motor spin-up which should be well within spec.
I've been through VE.Configure and loosened the DC input low threshold down to 11.5V, but I'm still getting the trips. My suspicion is there's a voltage sag on the 16mm² cable run between the battery and inverter — it's about 1.2 metres but I've got an Anderson connector in there that I'm not 100% confident about. Could a dodgy connector really cause enough of a drop to spook the inverter?
The washing machine is an Indesit 6kg, nothing exotic. It's the motor starting current that seems to be the culprit — I've read these can spike to 6-7x running current for a split second. Has anyone managed to tame this with the assistants in VE.Configure, or is it more of a wiring/connection issue I need to sort first before messing with settings?