Anyone else had grief with a Victron MultiPlus 12/3000 tripping on washing machines?

by Lisa · 2 weeks ago 143 views 7 replies
Lisa
Lisa
Active Member
10 posts
Joined Mar 2025
2 weeks ago
#7856

Right, I'm at my wits' end with this. My MultiPlus 12/3000/120 keeps throwing a low battery alarm and cutting out about 3-4 minutes into a wash cycle. I've got 400Ah of lithium (Winston cells, 4S configuration) sitting at around 80% SOC when it happens, so it's not like the batteries are gasping. The inverter's pulling around 1,800W during the motor spin-up which should be well within spec.

I've been through VE.Configure and loosened the DC input low threshold down to 11.5V, but I'm still getting the trips. My suspicion is there's a voltage sag on the 16mm² cable run between the battery and inverter — it's about 1.2 metres but I've got an Anderson connector in there that I'm not 100% confident about. Could a dodgy connector really cause enough of a drop to spook the inverter?

The washing machine is an Indesit 6kg, nothing exotic. It's the motor starting current that seems to be the culprit — I've read these can spike to 6-7x running current for a split second. Has anyone managed to tame this with the assistants in VE.Configure, or is it more of a wiring/connection issue I need to sort first before messing with settings?

Cumbrian OffGrid
Cumbrian OffGrid
Member
6 posts
Joined Jan 2025
2 weeks ago
#15274

CumbrianOffGrid replied:

@Lisa1978 Classic symptom this. Three to four minutes in is almost certainly when the drum heats the water - that's when the heating element kicks in and absolutely hammers your battery. A washing machine might start at 500W but the element can pull 2kW+ simultaneously with the motor load.

With Winston cells I'd check your BMS discharge current limit first - it might be set conservatively and signalling low voltage to the MultiPlus before your actual battery is anywhere near depleted.

Also worth checking your battery cable cross-section and connection quality between cells. Voltage sag under that kind of surge can look like a low battery condition even with healthy cells.

Cold wash cycles are your friend off-grid honestly - cuts that element load entirely. What temperature are you washing at currently?

Anglia Solar
Anglia Solar
Member
5 posts
Joined Dec 2025
2 weeks ago
#15321

AngliaSolar replied:

@Lisa1978 Worth checking your MultiPlus settings in VE.Configure — specifically the DC input low shutdown voltage. A lot of units ship with defaults suited to lead-acid, so if yours is set around 11.5V it'll trip the moment your lithium sags under load, even if the cells are genuinely healthy and well above empty.

Also, what BMS are you running on those Winston cells? If it's cutting the DC side before the Victron even has a chance to react, you'll get exactly the symptoms you're describing. The BMS log (if yours has one) would tell you whether it's the inverter protecting itself or the BMS pulling the plug.

@CumbrianOffGrid is on the right track about timing — that heating element kicking in is brutal on instantaneous draw.

Chris
Chris
Member
1 posts
Joined Mar 2025
2 weeks ago
#15394

Chris1966 replied:

@Lisa1978 Had almost identical grief with mine last winter. One thing nobody's mentioned yet — what cable size are you running between your batteries and the MultiPlus? I was getting phantom low voltage alarms that turned out to be voltage drop across undersized cable rather than the battery actually being low. Swapped from 35mm² to 70mm² and it was night and day. Also worth checking your bus bar connections are properly torqued — loose connection can cause a sudden voltage spike under load that the BMS reads as a fault. What does the battery voltage actually show in the Victron app during the cutout? If it's recovering quickly after the trip that points to a cabling/resistance issue rather than actual battery capacity.

Marine Mike
Marine Mike
Member
6 posts
thumb_up 1 likes
Joined Dec 2024
1 week ago
#15597

MarineMike replied:

@Lisa1978 One thing I'd add — check your actual cable runs and connections before diving too deep into settings. I had similar dropouts on my boat install and it turned out to be a dodgy crimped lug on the negative busbar. Volt drop under surge load was enough to trigger the protection even though resting voltage looked fine.

Grab a decent clamp meter and log the DC voltage at the MultiPlus terminals during the fault, not just at the battery. If you're seeing more than 0.3–0.4V difference between those two points you've got a wiring issue, not a battery or settings problem.

Winston cells should handle washing machine inrush no bother if everything else is solid — they're decent cells.

Russ Mitchell
Russ Mitchell
Active Member
12 posts
thumb_up 1 likes
Joined May 2024
1 week ago
#15829

RussMitchell75 replied:

@Lisa1978 Something worth checking that nobody's touched on yet — what's your BMS set to for discharge current limits? Winston cells can handle serious current but if your BMS is configured conservatively (say 100A continuous) it might be cutting the legs out from under the inverter right when the wash motor kicks into a heavy cycle. Also, what cable gauge are you running from the battery to the MultiPlus? I'd want at minimum 70mm² for a 3000VA inverter, ideally 95mm². Voltage drop on undersized cable can trigger the low battery protection even when the cells themselves are perfectly happy. Worth sticking a clamp meter on the DC side during a cycle if you can.

Bramble Hermit
Bramble Hermit
Active Member
10 posts
Joined Aug 2025
1 week ago
#15811

BrambleHermit replied:

@Lisa1978 Something worth considering that hasn't been mentioned — what's your battery temperature like? Winston cells can see a noticeable drop in peak discharge capability in colder conditions, and if your setup is in an outbuilding or van, even 10°C can make a meaningful difference to how the BMS responds under that initial motor surge. Also, are you running the washing machine on a programme with a high-temperature wash? The heating element kicking in simultaneously with the drum motor is a proper double-whammy on draw. Try a cold 30° cycle and see if the behaviour changes — it's a useful diagnostic step before you start tweaking inverter parameters. Helped me isolate a similar fault on my own setup last year.

OldSailor78
OldSailor78
Active Member
11 posts
thumb_up 3 likes
Joined Dec 2024
4 days ago
#16432

Had this exact issue in my motorhome last winter. Turned out my MultiPlus low battery cutoff was set too conservatively — it was tripping at 12.2V which, under the surge load of a washing machine motor, was getting hit almost immediately even with healthy cells.

Worth checking your Low DC Alarm and Low DC Shut-down thresholds in VE.Config. Winston cells can handle being pushed harder than the Victron defaults assume. I dropped mine to 11.8V shutdown and the problem vanished overnight.

Also — what size are your DC cables? Even slight undersizing causes enough voltage drop under surge to trigger the alarm well before your actual battery is in trouble.