I've been running a Victron Multiplus 2 48/3000/35 in my off-grid setup for about eight months now and it's been mostly brilliant, but I keep getting nuisance trips when I fire up my kettle and the air fryer at the same time. We're talking roughly 2,800W combined, which should theoretically be within the 3,000W continuous rating, but the unit cuts out within about 30 seconds every single time.
The battery bank is 280Ah of CALB LiFePO4 cells wired in series for 48V, so roughly 13.4kWh usable. I've checked the cabling and it's all 70mm² from the batteries to the inverter with proper lugs, so I don't think voltage drop is the culprit. Ambient temp in the cabinet is around 18°C, so overheating seems unlikely too.
I had a dig around in VictronConnect and noticed the low battery voltage alarm was flickering briefly during the trip — it showed something like 47.1V momentarily. I'm wondering if the BMS is throttling the discharge current and the inverter is seeing that as a low voltage condition rather than an actual battery problem. My BMS is a JK 200A unit and I haven't touched the default settings since I built the pack.
Has anyone seen similar behaviour, or does anyone know whether tweaking the "DC input low shut-down" threshold in VE.Configure would help here? I'm also curious whether setting up proper DVCC between the BMS and the Multiplus might smooth things out.