Been running my off-grid cabin setup for about eight months now and it's been mostly brilliant, but I keep hitting an annoying snag. Whenever someone boils the kettle (2.8kW) at the same time as the microwave kicks in (800W), the MultiPlus-II 48/3000 throws an overload fault and shuts down. Total combined load should only be around 3.6kW, which I'd have thought was within spec — the inverter's rated at 3kW continuous with a 6kVA peak, so I expected it to handle short spikes no bother.
I'm on a 48V bank, eight 200Ah LifePO4 cells wired in series, so the battery side seems solid enough. The DC cabling is 70mm² all the way to the bus bars, so I don't think it's a voltage sag issue causing false trips. I've had a look through VEConfigure and I haven't touched the overload trip threshold — it's sitting at the default.
Has anyone actually adjusted the PowerControl or dynamic current limiter settings to give a bit more headroom for these kinds of inrush spikes? I've seen a few mentions of tweaking the AC input current limit but I'm not sure that's even relevant here since I'm running island mode 99% of the time with no shore power connected.