Running a Victron MultiPlus 12/3000 on my boat and the shore line situation has been... educational. The main issue I kept hitting was the input current limiter not playing nicely with older marina pedestals that have genuinely soft supplies — voltage sagging to 210V under load, which then triggers the unit to start supplementing from the batteries rather than charging them. Took me an embarrassingly long time to figure out why my Fogstar lithium bank kept sitting at 70% despite being plugged in overnight.
A few things that helped:
- Dropping the input current limit to 10A rather than leaving it at 16A — counterintuitive but it stabilised everything
- Enabling the weak AC input setting in VictronConnect, which is genuinely designed for exactly this scenario
- Checking the shore power cable — a corroded 16A blue connector was adding measurable resistance and making the sag worse
The other thing worth flagging is earth leakage. Older marina installations can have questionable earthing, and if you've got a galvanic isolator fitted (you should have one), it's worth testing it periodically. Mine had failed silently.
Anyone else finding particular marina brands worse than others? I've noticed a couple of the older Canal & River Trust facilities near us are noticeably worse than the privately run ones.
Also curious whether anyone's running a Quattro instead — the dual AC input looks appealing if you want to combine shore power with a generator without manual switching.