Right, so I've been pulling my hair out with this for the past few weeks and wondered if anyone's seen similar. I've got a Victron MultiPlus 12/3000/120-50 running off a 200Ah LiFePO4 bank (2x 100Ah Epoch batteries in parallel). Everything's been absolutely fine for months, but lately the inverter keeps tripping on what I can only describe as perfectly reasonable loads.
The specific trigger seems to be running my 2kW kettle at the same time as my 700W microwave. That's only around 2.7kW combined, well within the 3kVA rating of the unit. The MultiPlus throws a low battery warning (flashing red/yellow) and shuts down, even though my Victron BMV-712 is showing the bank at 96-98% SoC and resting voltage around 13.2V. Genuinely baffling.
I've been into VictronConnect and had a look at the settings, and I'm wondering if the DC input low shutdown voltage is set too conservatively from factory. The kettle element presumably causes a sharp inrush that momentarily drags the voltage down, and perhaps the MultiPlus is reacting to that transient rather than the true battery state. Has anyone tweaked the low voltage cutoff or the restart voltage thresholds to account for this kind of spike?
Worth mentioning the cables are 70mm² and runs are pretty short — about 600mm from battery to inverter — so I don't think it's a cable resistance issue. Would love to know if this is a settings thing or something more fundamental I'm missing.