Fitted a Multiplus-II 24/3000/70 in my narrowboat setup about three months ago, paired with 400Ah of lithium (Fogstar Drift cells) and a 60A Cerbo GX running everything together. On paper it should handle my 2.5kW inverter load no bother, but I keep getting nuisance trips when I fire up the microwave and the induction hob at the same time — roughly 2,200W combined. The unit throws a low battery warning even though the SOC is showing 85-90% on the Cerbo display.
I've been through the VE.Configure settings and dropped the DC input low voltage threshold down from 23.5V to 22.8V, which helped a bit but hasn't cracked it. My cable run from the battery bank to the Multiplus is about 1.8 metres each way, using 70mm² tinned copper, so I don't think volt drop on the cables is the culprit. The Fogstar BMS is set to a 200A discharge limit, which should be plenty.
Has anyone seen this with a similar setup, or know whether it's worth looking at the dynamic current limiter settings in VE.Configure? I'm wondering if the Multiplus is reacting to a voltage sag at the battery terminals that the Cerbo isn't catching fast enough. Any pointers would be brilliant.