Been scratching my head over this one for a few weeks now. I've got a MultiPlus II 48/3000/35 hooked up to a 48v 200Ah LiFePO4 bank (Gobel cells, 16s), and it keeps cutting out when I run the kettle and microwave at the same time — around 2,800W combined. The inverter just trips and throws an overload warning in VictronConnect, even though we're well within the 3,000VA rating on paper.
I've gone through the usual suspects — checked all my cable runs (35mm² throughout, kept under 1.5m from battery to inverter), terminals are tight, BMS isn't the one tripping (confirmed via the Daly app). Battery voltage under load is sitting around 51.2v, so it's not a low voltage cutoff issue. The odd thing is it only seems to happen when both appliances kick in within a second or two of each other, suggesting it might be an inrush current spike rather than a sustained overload.
Has anyone played around with the assistants in VEConfigure to soften the overload response, or adjusted the PowerControl settings? I've seen mention of tweaking the "overload trip time" but I can't find a definitive answer on whether that's actually exposed for the MultiPlus II or just the older units. Also wondering if staggering the loads with a simple timer relay on the kettle socket would be a reasonable workaround rather than faffing with the firmware.
Would love to hear if anyone's cracked this — or if I'm missing something obvious.