We've been off-grid on our smallholding in mid-Wales for about 18 months now, running a 48V system with a 560Ah lithium bank and a 3kW array. The MultiPlus-II 48/3000 has been absolutely solid until recently — now it's tripping on overload pretty much every time I try to run the kettle (2.2kW) and microwave (900W rated, but apparently pulls closer to 1.5kW on startup) at the same time. That's only around 3.7kW combined, and the inverter is rated for 3kVA continuous with a 6kVA surge, so in theory it should cope.
I've updated the firmware via VE.Config and checked the AC out wiring — all looks fine. The battery voltage is sitting at a healthy 52–53V under load, so I don't think it's sagging to the point of triggering the low voltage cutoff. The tripping happens almost instantly when both loads kick in together, which makes me think it might be a settings issue rather than a hardware fault. The overload trip level in VE.Config is currently set to the default — I haven't touched it.
Has anyone adjusted the overload trip delay or threshold on theirs, or is there something obvious I might be missing? Also wondering whether the assistants (PowerAssist etc.) could be interfering somehow, though we're not connected to the grid out here so that seems unlikely. Any thoughts welcome.