Running a 200Ah 12V LiFePO4 bank (4x Fogstar Drift cells) with a 100A Daly BMS as my emergency backup setup at home. Everything's been solid for months — Victron SmartShunt monitoring, all balanced nicely, resting voltage bang on 13.3V. But last week I put a 1500W inverter load on it (oil-filled radiator test during a grid outage) and the BMS tripped out cold. No warning, just dead. Reset fine, but did it twice more under the same load.
The maths should work — 1500W ÷ 12V is 125A, so I'm right at the edge of the 100A rating. What I can't work out is whether the Daly is being overly conservative on its overcurrent threshold, whether there's a voltage sag issue triggering the low-voltage protection prematurely, or whether the BMS just can't sustain that continuous current even if the peak is technically within spec. My cable runs are 35mm² so I don't think that's the issue, but I haven't ruled out connection resistance at the terminals.
Has anyone tuned the overcurrent and undervoltage trip points on a Daly via the PC software? I'm wondering if the default settings are quite conservative out of the box. Alternatively, is this just a case of needing to step up to a 150A or 200A unit — JK BMS seems popular here for active balancing builds, though I'd rather not rewire if I can avoid it.