Running a MultiPlus-II 48/3000 with a 16kWh Fogstar Drift LiFePO4 bank and it keeps tripping when I fire up my workshop compressor (about 2.2kW startup surge). Inverter's set to 3000W continuous so I'd expect it to handle it, but nope — cuts out within seconds every time.
Checked the DC cabling and it's all 70mm² with decent Anderson connectors, so I don't think it's a voltage sag issue. Assistant switch is off. Wondering if it's the overload trip threshold in VE.Configure that needs tweaking, or if the compressor inrush is just hitting too hard even for a 3kVA unit.
Anyone dialled in their overload settings for motor loads? Feels like there should be a way to give it a bit more headroom without voiding the warranty or cooking anything. What settings are you running?