Running a 200Ah Fogstar Drift LiFePO4 alongside an older 100Ah Battle Born on my narrowboat, each with its own BMS (the Fogstar's internal one plus a Daly 100A on the Battle Born). They're wired in parallel through a Victron SmartShunt sitting between the bank and the 12V bus. Overall capacity reads fine on the Victron and the Cerbo GX sees both, but I'm getting occasional cell voltage discrepancies between the two banks that I suspect are causing one BMS to throttle charge before the other is full.
The symptom is the Victron MPPT backing off around 13.8V when I'd expect it to push to 14.2V absorption — I think the Fogstar's internal BMS is hitting its high-voltage threshold slightly earlier than the Daly, effectively dragging the whole parallel bank down. Checked the Daly settings via the PC software and it's set to 3.65V per cell cutoff, but I've no visibility whatsoever into the Fogstar's internal limits.
Has anyone solved this properly — either by rebalancing the banks before paralleling, or by just accepting that mixed BMS setups need separate charge circuits? Considering splitting them onto separate Victron MPPT outputs but that feels like overkill on a boat where I'm already juggling a 40A shore power charger, a B2B from the engine, and two 175W roof panels.