Anyone know if a 200Ah lithium battery will run a small chest freezer overnight?

by FormerMariner36 · 3 weeks ago 24 views 5 replies
FormerMariner36
FormerMariner36
Active Member
16 posts
thumb_up 3 likes
Joined Nov 2024
3 weeks ago
#18802

Running a small chest freezer off-grid is something I've been mulling over for the boat, so curious whether anyone's actually done the maths on this properly.

My situation: I've got a 200Ah LiFePO4 (Fogstar Drift) sitting in the garden office setup, and over winter I'm planning to repurpose some of that capacity for a small chest freezer — something like a 60-litre unit. The office draws very little overnight, so theoretically there should be headroom.

From what I can work out, a decent small chest freezer might pull around 30-40W when the compressor's running, but obviously it cycles on and off rather than running continuously. I've seen figures suggesting maybe 0.5–1 kWh per 24 hours for a well-insulated unit, which on paper looks manageable.

What I can't quite figure out:

  • How much of that 200Ah is realistically usable overnight without hammering the battery (staying above 20% SOC)?
  • Does the compressor start-up draw cause any issues with a standard 1000W inverter?
  • Is there a meaningful difference between running a purpose-built 12V compressor fridge versus a mains chest freezer through an inverter, efficiency-wise?

I've got Victron kit managing everything, so the monitoring side is covered — I just don't want to find out the hard way that I've been naive about the actual consumption figures.

Anyone running something similar, either on a boat or off-grid building? Real-world numbers would be far more useful than spec sheets at this point.

Holly Gazer
Holly Gazer
Active Member
16 posts
thumb_up 10 likes
Joined Aug 2023
3 weeks ago
#18826

@FormerMariner36 really depends on the freezer's actual consumption rather than its rated wattage — they cycle on and off so the duty cycle matters massively. Have you checked if yours has an energy label with kWh/24hrs? That's the most reliable starting point.

For my garden office setup I use a Fogstar Drift 200Ah and I've found real-world draw is always higher than I'd budgeted for once you factor in ambient temperature (freezers work harder in warm weather).

A few questions worth thinking through:

  • What's the freezer's actual kWh/24hr figure?
  • What's your usable DoD — are you going to 80% or deeper?
  • Any solar topping up overnight, or fully standalone?

200Ah could work but I'd want to see the numbers before committing. What freezer model is it?

RetiredChef71
RetiredChef71
Active Member
10 posts
thumb_up 2 likes
Joined May 2024
2 weeks ago
#18853

Good point from @HollyGazer about actual consumption. From my cabin setup I'd add — ambient temperature matters massively. My chest freezer pulls maybe 30-40Wh per hour in a cool outbuilding, but when I had it in a warmer space that crept up considerably.

On a 200Ah LiFePO4 you've realistically got around 190Ah usable (LiFePO4 is brilliant for this). At 12V that's roughly 2.28kWh. A decent small chest freezer overnight (say 10 hours) might use 300-500Wh depending on ambient and how full it is.

You should be absolutely fine in most scenarios — that's only 15-25% of your capacity gone.

Fogstar do a decent 200Ah if you're shopping around. I'd also suggest a smart shunt (Victron BMV-712) so you actually know what's happening rather than guessing.

Panel Dan
Panel Dan
Member
8 posts
thumb_up 5 likes
Joined Dec 2024
2 weeks ago
#18875

Ran this exact experiment on my narrowboat last summer. The chest freezer I had — a small 60L unit — was pulling around 30–40Ah per 24 hours in decent ambient temps, so overnight (say 8 hours) you're looking at roughly 10–15Ah in practice. Your 200Ah bank has that covered easily, even accounting for BMS overhead and only drawing to 80% usable capacity.

The variable nobody's mentioned yet is compressor start-up surge — worth checking your BMS can handle the brief spike without tripping. Most decent LiFePO4 packs manage it fine, but I've seen cheaper units hiccup on this.

Also worth fitting a small Victron BMV monitor if you haven't already — takes the guesswork out entirely and you'll actually know what your freezer costs you each night rather than estimating.

Defender Solar
Defender Solar
Active Member
30 posts
thumb_up 6 likes
Joined Jun 2023
2 weeks ago
#18899

Great thread — this is exactly what I spent a sweaty August weekend testing in my shepherd's hut conversion.

One thing nobody's mentioned yet: duty cycle varies wildly by how full the freezer is. Mine ran noticeably longer between cycles once I'd packed it out with frozen water bottles. More thermal mass = less work for the compressor.

On a 200Ah LiFePO4 (assuming you're not dropping below 20% SOC) you've realistically got around 160Ah usable. A well-packed small chest freezer in moderate temps should sit comfortably within that overnight — but I'd stick a Victron SmartShunt on it first and actually log a 24-hour cycle before committing.

@PanelDan's narrowboat data is gold — ambient temps on a boat hull can be surprisingly forgiving in summer compared to a static caravan baking in direct sun.

CE_Builds
CE_Builds
Regular
69 posts
thumb_up 40 likes
Joined Oct 2023
2 weeks ago
#19021

Done this on both my garden office and the boat, so can chip in properly.

The maths that catches people out: it's not just the watt-hours, it's duty cycle vs ambient temp. A well-insulated chest freezer in a cool bilge space might only run 20-30% of the time. Same unit in a hot engine room or sunny cockpit locker? Could be 60%+.

On my boat I run a 40L Engel-style unit. Honest overnight draw (8hrs, cool environment) sits around 15-25Ah. Your 200Ah LiFePO4 — assuming you're not going below 20% SoC — gives you ~160Ah usable. So technically fine, but factor in your other loads too.

@PanelDan's narrowboat data sounds about right to me. Pre-cooling the freezer before you go off-grid makes a noticeable difference as well.