Running a pair of these in parallel in my motorhome build and trying to nail down the cabling spec before I commit to anything.
Each battery is rated for 200A continuous discharge, so theoretically with two in parallel I'm looking at 400A available from the bank. My inverter (Victron Multiplus-II 3000) pulls up to around 250A peak at 12V under heavy load.
Cable sizing question: I've got 70mm² tinned copper running from each battery to a busbar, then a single 95mm² run to the inverter. Is that sufficient, or should I be upsizing to 95mm² throughout? Runs are fairly short — roughly 600mm per battery to busbar, then about 800mm busbar to inverter.
Fuse placement:
- ANL fuse directly at each battery terminal (so two fuses total) — what rating? The Epoch V2-T has an internal 200A BMS but I presume I still need external fusing?
- Then a second ANL or MIDI fuse on the main positive leaving the busbar toward the inverter?
Victron's own documentation is a bit vague on parallel battery setups and I've not found anything Epoch-specific for UK installations.
Also wondering whether anyone's used Fogstar or another UK supplier for pre-made cable assemblies at these gauges, or whether it's worth getting them crimped locally.
Primarily concerned about getting the protection scheme right rather than just "it works" — want proper fault protection at each battery independently.