Anyone else's Cerbo GX and BMS playing a game of "who's right?" with the SOC figures?
Running a Fogstar Drift 16kWh on the boat and my BMS reckons I'm at 78% whilst the Cerbo is confidently displaying 64% — both can't be correct, and frankly neither inspires confidence.
The core issue as I understand it (pedant hat firmly on):
- The Cerbo/CCGX calculates SOC via coulomb counting from a shunt, or trusts the BMS over the VE.Bus depending on your settings
- Without a Lynx Shunt (or SmartShunt) in the loop, you're essentially letting the Multiplus II make educated guesses
- The BMS SOC is calculated internally and may not account for the same charge/discharge cycles your Victron kit sees
My shepherd's hut setup has a SmartShunt fitted and the two figures stay within 2-3% of each other — probably not coincidental.
Worth checking Device List → System → DVCC settings and whether "Use solar charger current to improve VE.Bus SOC" is ticked, as that can cause drift if your MPPT isn't reporting cleanly.
Also: has the BMS done a proper full charge cycle to calibrate itself? A fresh installation SOC is basically fiction until it's seen at least one full top-up to absorption.
Curious whether anyone running BasenGreen packs specifically has cracked this — their BMS comms over CAN seem a bit inconsistent from what I've read.