Had this exact headache last winter fitting out my garden office — the 800va Multiplus only has the one VE.Bus port, and you're basically playing a game of "who gets the chair" between the VE.Bus BMS and the Cerbo GX.
Ended up using the VE.Bus BMS Assistant loaded onto the Multiplus itself, which lets the Cerbo talk to the inverter via VE.Bus while the BMS handles its charge/discharge allow signals through the dedicated Charge Disconnect and Load Disconnect terminals instead. Means you're not trying to daisy-chain two devices onto a single port like some kind of cursed spaghetti junction.
Key bits that caught me out:
- Make sure you're running the VE.Bus BMS v1 wiring properly — the
Allow to ChargeandAllow to Dischargewires go to the Multiplus ATC/ATD inputs, not the VE.Bus port itself - Load the correct Assistant via VEConfigure before you connect anything live
- The Cerbo then just sits on VE.Bus solo and plays nicely
Anyone else running the older BAT512 series batteries with this combo? Curious whether others had to fiddle with the low-cell cutoff settings because mine was tripping the BMS at what felt like perfectly reasonable temperatures for a draughty British shed.
Would love to know if there's a cleaner way — Victron's own docs are about as clear as a November morning in Manchester. 🌧️