Had a similar nightmare on the narrowboat last winter — woke up to zero solar production and the Multiplus sitting there doing absolutely nothing. Turned out to be an internal fault flag that had quietly killed the whole system overnight.
Setup at the time was:
- 4 × 175W panels (not massive, but enough for the boat)
- Multiplus 12/3000
- Fogstar Drift 200Ah LiFePO4
- Cerbo GX for monitoring
The Cerbo was showing a vague internal fault code but VRM wasn't giving me much to go on remotely. What actually fixed it was a full power-down — disconnected the battery, waited a proper 60 seconds (not the "count-to-ten" version), then brought everything back up in the right sequence. Panels last, obviously.
Worth checking:
- Has the inverter thrown an internal fault in the history log? Pull it up in VictronConnect properly, not just the dashboard overview
- Pylontech comms — if the BMS and Multiplus have lost their handshake, the inverter can just... stop. Check the VE.Bus to BMS communication is solid
- Firmware — had a mate with a US3000C where a firmware mismatch between the Multiplus and the CCGX caused intermittent shutdowns
The Pylontech/Multiplus combo is generally rock solid but it's surprisingly sensitive to that BMS communication link. Anyone else seen this on a 48V system specifically? Curious whether it's more common at that voltage.