Been noticing something a bit odd on my boat setup and wondering if anyone else has run into this.
I'm running a Renon BMS talking to a Cerbo GX via VE.CAN, with a Multi RS in the mix. The problem is the SOC readings don't agree with each other — the BMS is reporting one figure, the Multi RS is showing something different, and the Cerbo is essentially picking a side rather than consolidating them properly.
From what I can tell, the Multi RS does its own internal SOC calculation based on charge/discharge history, whereas the Renon BMS is reporting cell-level data directly. When they disagree — which seems to happen after a partial cycle or if the battery hasn't hit a proper absorption/float in a while — the Cerbo ends up displaying something that doesn't match either source accurately.
A few things I've tried:
- Setting the DVCC source priority to the BMS
- Forcing a full charge cycle to let everything re-sync
- Checking VE.CAN termination (both ends properly terminated)
The BMS figures feel more trustworthy to me since it's pulling directly from the cells, but I'm not 100% sure the Multi RS is respecting that as the master SOC source.
Anyone running a similar architecture — particularly with VE.CAN rather than VE.Bus — seen this? Is there a Victron setting I'm missing that forces the Multi RS to defer to the BMS entirely, rather than blending or overriding?
Would be good to know if this is a known quirk or something worth raising with Victron support.