Running a small chest freezer on my narrowboat overnight and wondering if my single 200Ah (Fogstar Drift 12V) is going to cope, or if I'm about to wake up to a puddle of defrosted disappointment.
The freezer is a Subcold Ultra 60 — pulls about 60W when the compressor kicks in, but obviously it's not running constantly. From what I can tell it cycles maybe 30-40% of the time once it's up to temperature, so rough maths says something like:
- 60W × ~35% duty cycle = ~21W average draw
- Over 8 hours = ~168Wh
- At 12V that's roughly 14Ah
Which sounds fine — 200Ah lithium at 80% DoD gives me 160Ah usable, so 14Ah should be nowt. But I'm skeptical of my own optimistic maths, because I've been wrong before (RIP my old AGM bank, 2019–2021, gone too soon).
Questions I'm actually not sure about:
- Does a chest freezer's compressor have a nasty startup surge that causes any real-world issues with a Victron MultiPlus 12/1200?
- Is a 35% duty cycle realistic for a chest freezer in a UK autumn, or am I being naive?
- Anyone actually done this and got data from a Victron Cerbo or similar to share?
The boat's solar will be basically useless overnight obviously, so it's purely battery capacity I'm relying on. Generator top-up in the morning is an option but I'd rather not run it daily if the numbers genuinely work.