Had something similar crop up on my narrowboat setup last year, though single-phase rather than three-phase. Running a MultiPlus-II 48/3000 with a bank of batteries and they kept dropping into protection mode on startup — that little LED would flash on, system would refuse to play ball.
Turned out to be a pre-charge issue. The inverters were pulling enough inrush current on startup to spook the BMS into thinking something was seriously wrong. A few things that helped me get it sorted:
- Staggered the startup sequence rather than everything coming on at once
- Checked the BMS comms were actually talking to the Cerbo GX properly (DVCC settings were a bit off)
- Made sure battery temp was above the minimum threshold — narrowboat in February isn't exactly warm
For a three-phase setup with three MultiPlus-IIs, I'd imagine that inrush is significantly worse since you've effectively got three inverters all demanding current simultaneously. Are your Dyness units connected via CAN bus to the GX device? If the BMS isn't handing off state-of-charge data properly, the system can behave oddly on startup.
Also worth checking:
- VEConfigure — is ESS assistant configured identically across all three inverters?
- Firmware all matching on the MultiPlus units?
Anyone else running Dyness with Victron three-phase? Curious whether this is a known compatibility quirk or more of a config issue. Would be useful to know what firmware version the Dyness BMS is on as well.