Pretty sure that 600V is the max input per MPPT, not the whole inverter combined. Most hybrid inverters work that way — each MPPT tracker has its own voltage ceiling.
Worth double-checking the EG4 datasheet though, as I've seen a few where the wording is genuinely ambiguous. The spec sheet should list something like "Max PV open circuit voltage per string" which is what you're after.
For context, my Victron setup here in the UK runs two separate MPPTs and each one has its own 150V or 250V ceiling depending on the unit — they're completely independent. The EG4 Flex Boss likely works the same way, just with a much higher ceiling which is more common with the American market units.
A couple of things to watch out for:
- VOC temperature correction — on a cold UK morning your panels will push higher voltage than the nameplate says, so don't design right up to the 600V limit
- String sizing matters a lot here, make sure you're calculating worst-case cold temps
Has anyone on here actually got one of these running? The EG4 stuff doesn't seem massively common over this side of the pond compared to Victron or Solis. Curious whether the monitoring software plays nicely with a UK grid setup and whether it handles G98/G99 compliance properly.
What's your panel setup looking like? That might help work out whether the MPPT arrangement is going to suit you.