Been wrestling with this exact scenario on my static caravan setup recently, so thought it'd be worth opening it up for discussion here.
Running a Multiplus-II 48/3000 with a SmartSolar MPPT 150/35 and a Cerbo GX managing the whole lot. Battery bank is Fogstar Drift 48V cells configured in the VEConfigure ESS assistant.
The bit I keep second-guessing is the Charge Voltage Limit (CVL) parameter in the ESS settings — specifically when it actually triggers the MPPT to back off and start curtailing charge current. My understanding is:
- CVL is broadcast over the VE.Bus/DVCC network as the upper voltage ceiling
- Once battery voltage hits CVL, the MPPT should ramp down to maintain that ceiling rather than push past it
- But in practice I'm seeing the MPPT occasionally overshoot by 0.2–0.3V before it reacts
Is anyone else seeing this lag? I'm wondering if it's a DVCC polling interval issue or whether my CVL is simply set too close to the absorption voltage, leaving no headroom for the system to respond cleanly.
Also curious — for those running LiFePO4 without a proper BMS-to-Cerbo comms link (i.e., no CANbus, just manual DVCC settings), how are you determining your CVL value? I've been setting it 0.2V below the BMS high-voltage cutoff, which feels conservative but I've no real benchmark to compare against.
Would be genuinely useful to compare configs. What DVCC and ESS charge parameters are others using on similar Victron setups?