Had a spell last autumn where my Multiplus-II 24/5000 was throwing overload faults seemingly out of nowhere — no massive load spike I could identify, batteries looking healthy on the Victron display, everything appeared fine. Took me a good few evenings of head-scratching before I started suspecting the BMS communication rather than the inverter itself.
The thing is, when your BMS throttles charge/discharge limits and the Multiplus doesn't get that signal cleanly via the VE.Can or BMS assistant config, it can behave oddly under load. Mine turned out to be a dodgy RJ45 cable between the Fogstar Drift battery and the GX device — looked perfectly fine physically, but was causing intermittent dropouts.
A few things worth checking if you're seeing random overloads on a 24V system:
- Actual battery voltage under load — not just resting voltage
- Whether your BMS is cutting out momentarily and the inverter is seeing a sudden voltage collapse
- ESS or inverter assistant settings — particularly the DC input low shutdown thresholds
- Cable quality on your comms connections, not just the power runs
I'd also say: don't immediately blame the inverter. These units are generally solid. It's usually something upstream.
Anyone else had overload gremlins on a 24V Multiplus setup? Curious whether others found BMS comms to be the culprit or whether there were other causes I haven't considered. Would be good to build up a proper list of causes in this thread.