Similar story here, actually. Been running a Victron MultiPlus-II 48/5000 with a Fogstar Drift 16kWh in my cabin setup for about eight months now, and around month four I started getting these mysterious shutdowns — no obvious pattern, no screaming alarms, just... off.
What made it maddening was the timing. Three trips in a fortnight, then nothing for weeks.
Here's what eventually helped me piece it together:
VRM Portal logs — if you've got a Cerbo GX, dig into the detailed logs around the exact minute of each trip. Mine revealed brief voltage sag events I'd completely missed on the dashboard glance.
Check your BMS communication — the Fogstar units talk over CAN bus to the Cerbo. I had a dodgy cable seating that was causing the Cerbo to occasionally lose the BMS signal, which triggered a protective shutdown. Reseated the RJ45 and the problem vanished.
Load spikes — are you running anything that kicks in hard? My EV charger on a timer was occasionally starting up during a period of low solar and high background load. The MultiPlus didn't like that combination one bit.
A few questions worth asking yourself:
- Has anything changed in your setup or routine in the last month?
- What does the Fogstar BMS app show around the trip times?
- Any new loads added recently?
The Enphase microinverter angle is interesting too — had anyone considered whether a grid-forming conflict could be involved if you're in any kind of hybrid setup?
Would love to know what others have found. These intermittent faults are the worst to chase down.