So here's a frustrating one. I've had a Fogstar Drift 200Ah sitting in the motorhome for about eight months now, generally brilliant, no complaints — until I started using a Type 2 portable EVSE to top up the car from the motorhome's 230V inverter. The battery BMS trips out somewhere between 18 and 22 minutes into a charging session, every single time. Victron MultiPlus 2 3000VA on the inverter side, Fogstar's own BMS doing its thing on the battery side.
I've checked the obvious stuff. The draw is around 1,800–2,000W sustained, which is well within the Multiplus spec and should be within the Drift's 100A continuous discharge rating (sitting at roughly 78–85A at 24V). Temps are fine, well within operating range. The BMS isn't throwing a temperature fault — it just goes into protection mode silently and the whole lot drops off.
My suspicion is it's a sustained-discharge timeout rather than a true overcurrent event, but I haven't been able to confirm that with Fogstar yet. Their support response times have been a bit patchy to put it politely. Has anyone pulled apart the Drift's BMS parameters or got comms working with it to see what's actually triggering the cutoff?
Wondering if this is an EV charging specifically — something about the load profile being particularly unforgiving — or whether I'd see the same behaviour running a big inverter generator or similar sustained draw.