Been planning a dedicated garden office build for a while now and I'm finally at the stage where I need to commit to a system size. The structure is going to be a 4.8m x 3m timber-framed cabin, well insulated (100mm Rockwool, 50mm PIR in the floor). Primary loads will be a laptop, two monitors, a small NAS box, LED lighting, and a 1.2kW oil-filled radiator for winter. I've modelled the daily consumption at roughly 2.5–3kWh in summer and up to 6–7kWh on a cold winter day when the heater is running most of the time.
My current thinking is 4× 400W panels (1.6kW peak) on a south-facing 20° pitch roof, feeding a Victron SmartSolar MPPT 100/30, with a 5.1kWh Fogstar Drift 24V LiFePO4 battery. Inverter would be a Victron Multiplus-II 24/3000 so I've got the option to add grid backup later if planning permission for a cable run becomes a pain. The cabin is about 35m from the house, so a direct grid feed would need proper SWA cable and ideally some load calculations before I start digging.
The honest worry is January and February. Even with a decent battery, I know I'm going to be SOC-limited on back-to-back cloudy days up here (Peak District). Has anyone sized a similar setup and actually lived with it through a UK winter? I'm genuinely uncertain whether I should upsize to 6 panels and a second battery, or just plan from the outset for a small grid-tied charger as a backup kicker. The Multiplus-II obviously handles that natively, but it changes the planning situation.
Also curious whether anyone's paired a Victron setup with an immersion diverter for any excess summer generation — seems daft not to use it for domestic hot water given the cabin is close enough to