Had this exact issue last winter with my old Kipor 6.5kVA — turned out to be a combination of factors rather than just the AVR, so worth ruling a few things out before you spend money on parts.
First things to check:
- Fuel delivery — dirty carburettor jets or a partially blocked fuel filter can cause load-dependent dropout, especially mid-cycle when demand spikes
- Low oil shutdown sensor — these can give false triggers if the generator isn't level or the sensor itself is failing
- AVR capacitor — before replacing the whole AVR, check the capacitor on the exciter winding; they're cheap and fail regularly
- Load side — what's actually cutting out? The generator itself, or is the AVR losing regulation and your inverter/charger is tripping on under-voltage?
That last point is important. My Victron Multiplus was actually the thing "cutting out" — the generator was producing unstable voltage and the Multiplus was rejecting the input rather than the genny physically shutting down. Took me an embarrassingly long time to work that out via the VRM logs.
What make/model is yours, and what load were you running when it happens? Resistive loads like immersion heaters tend to be more forgiving than motor loads or inverter-driven equipment. Also — does it restart fine immediately, or does it need to cool down first? That points toward thermal protection kicking in versus fuel/electrical faults.
Worth grabbing a cheap clamp meter and logging voltage and frequency under load if you can — tells you a lot about whether the AVR is actually struggling or if it's something upstream.