Been wrestling with a similar setup in my tiny house build and wanted to get some collective wisdom going here.
Running a Victron MultiPlus-II 3000VA (24V) paired with Fogstar Drift 24V 200Ah LiFePO4 batteries, and I've been pulling my hair out with generator surging issues. My genny is a Honda EU22i (the UK equivalent of the 2200), and when the MultiPlus is in charge-only mode and the batteries are significantly depleted, the generator hunts noticeably — that classic rhythmic surging that sounds like it's about to give up.
From what I've diagnosed so far, the issue is the MultiPlus demanding charge current faster than the EU22i's inverter-generator can ramp up to meet it. The fix most people land on is ramping down the charge current in VE.Configure — I've dropped mine to 18A and it's settled considerably, though not entirely.
A few things I'm still investigating:
- PowerAssist calibration — whether tweaking the AC input current limit affects surge behaviour under combined load + charge scenarios
- UPS mode vs. charger-only mode — does it make a difference for generator stability?
- Whether the Dynamic Current Limiter setting in VE.Configure actually helps with inverter-generators specifically
This is primarily an emergency backup system for me, so the generator doesn't run often — but when grid goes down mid-winter I need it to work.
Anyone else running a Honda inverter-gen with a MultiPlus on a 24V system? Particularly interested in whether Cerbo GX + generator autostart changes the equation at all, since that's my next planned addition.