Anyone else running a Victron Multi or Quattro setup alongside a genny and finding the sync just decides to have a bad day for absolutely no reason?
Mine's considerably more modest than some of the three-phase beasts I've seen discussed elsewhere — just a single Quattro 48/5000 with a pair of Smartsolar 150/35s and a small Fogstar lithium bank — but the generator handshake still gives me grief occasionally when the grid input frequency drifts even slightly outside the Quattro's accepted window.
I've been reading about larger installs where blokes are stacking multiple Quattros across three phases with Fronius AC-coupled inverters thrown into the mix, and honestly the sync headaches there must be spectacular. One slightly grumpy Fronius and the whole thing presumably sulks like a teenager told to tidy their room.
For those of us on smaller UK setups, a few things that genuinely helped me:
- Tighten the AC input voltage/frequency range in VEConfigure — the defaults are quite forgiving but sometimes too forgiving
- Generator warm-up time set to at least 30 seconds before the Quattro attempts to sync
- Check your MK3-USB interface firmware is current — stale firmware caused me a phantom fault that had me baffled for a week
Is anyone running AC coupling with a Fronius or SolarEdge on a UK off-grid setup and actually getting clean sync? Or is "works fine until it doesn't" just the universal experience here?