Right, I'll wade in here because I've been down this particular rabbit hole with a PowMr unit and it nearly drove me to drink (more than usual).
The setting you're almost certainly wrestling with is the output source priority — most of these Chinese hybrid inverters have it buried under a menu that's labelled something different depending on which firmware revision they've shoved on it this week. On mine it was "Output Priority" and the options were SBU, SUB, and UTI. If you're off-grid or running backup, you want SBU (Solar → Battery → Utility/Generator).
The other one that catches people out is the battery type setting. If you're running lithium (Fogstar, Pylontech, whatever), make sure you're either on the User-defined setting or AGM — not Flooded — otherwise the charge voltages will be miles off and you'll wonder why your bank is sitting at 80% and the inverter's throwing a wobbly.
A few things worth checking on a 24v 3kw unit specifically:
- AC charging current — factory default is often stupidly high
- Battery low voltage cutoff — usually set too aggressively for LiFePO4
- Bulk/absorption/float voltages — absolutely need adjusting for your chemistry
What's the actual problem you're seeing? Error code, odd behaviour, won't switch modes? There are about forty-seven different PowMr 3k variants floating about and they're not all identical, so a bit more detail would help narrow it down considerably.