Ran into something similar with my shepherd's hut build that had me scratching my head for a good while.
I've got a Fogstar Drift 200Ah LiFePO4 behind a main isolator, with a Victron SmartSolar and a Victron IP22 shore charger both feeding in. What I noticed is that even with the isolator open, the DC bus downstream stays live — fridge, 12V lights, the lot. The chargers are effectively backfeeding through the load side and keeping everything energised.
It's not dangerous as such, but it does mean:
- The isolator isn't actually isolating anything whilst a charger is connected and active
- Any fault on the load side stays live even if you think you've killed the bank
- Slightly unnerving if you're doing any wiring work and assume the bus is dead
My current workaround is just disconnecting shore power and waiting for cloud cover before touching anything — not exactly elegant.
I think the proper solution is to either:
- Put the isolator between the chargers and the bus, not just between the battery and the bus
- Use a Victron BatteryProtect on the load side so loads drop off cleanly when the battery disconnects
But I'm curious whether anyone else has thought this through more carefully, particularly if you're running a BMS with a charge/discharge relay in the loop — does that change how you'd wire the isolator position?
Would be interested to hear how others have tackled it, especially on smaller off-grid setups where you don't necessarily want to over-engineer things.