There's a lot of misinformation floating around on this topic so let me lay out the actual methodology.
Start with your load, not your panels.
- List every device, its wattage, and daily hours of use. Sum it up — that's your daily Wh figure.
- Divide by your usable battery capacity (typically 80% for LiFePO4, 50% for lead acid) to get your required bank size.
- Your inverter VA rating needs to comfortably exceed your peak simultaneous load — not average. People consistently undersize here and wonder why their Victron Multiplus trips.
- Solar sizing: take your daily Wh requirement, divide by your peak sun hours for your UK location (realistically 2.5–3.5 in winter, not the 5hrs the marketing material quotes). Then add 25% for system losses.
In practice for my shepherds hut setup I ran through this properly — 1.8kWh daily load, 4.8kWh Fogstar Drift LiFePO4 bank, 800W of panels, Victron MPPT. Winter charging is still marginal but predictable because the maths was done first.
The inverter question specifically — size it for surge loads. Induction hobs and EV chargers have brutal startup draws. A 2kW continuous rating inverter might only handle 4kW surge for milliseconds.
What are others seeing for their actual winter peak sun hours in different parts of the UK? Would be useful to compile some real figures rather than relying on PVGIS estimates alone.