Good sizing question — this catches a lot of people out.
Start with your daily consumption in Wh. Pull your electricity bill and divide annual kWh by 365, or better yet, stick a plug-in energy monitor on your consumer unit for a week. Most UK homes land somewhere between 8–15 kWh/day depending on what you're running.
For 1–2 days backup, multiply that figure by 2, then apply your depth of discharge limit. With lithium (LiFePO4), you can realistically use 80–90% usable capacity. With lead-acid, drop that to 50% or you'll murder the cells within a couple of years.
Quick example:
- Daily use: 10 kWh
- 2-day backup: 20 kWh
- LiFePO4 at 80% DoD → 20 ÷ 0.8 = 25 kWh usable battery capacity
- At 48V, that's roughly 520Ah at 48V
For a home system at that scale, I'd be looking at Fogstar Drift 48V server rack batteries or building a bank from Eve/CATL cells with a decent Daly or ANT BMS. Victron Cerbo GX ties it all together nicely for monitoring.
Don't forget to factor in inverter efficiency losses (typically 5–10%) and seasonal solar variation — a UK winter will absolutely punish an undersized bank.
What loads are you planning to keep running during outages? Heating, EV charging, and immersion heaters change the maths dramatically. Worth listing them out so we can give more specific advice.