Had something similar with my 75/15 on the shepherd's hut last spring. The controller was showing absorption voltage but the amps were all over the place — kept dropping to near zero then spiking back up randomly.
Turned out to be a dodgy MC4 connector on the panel side rather than the unit itself. Worth checking those first before writing off the Victron. A loose or corroded MC4 can cause exactly the weird behaviour you're describing.
Few things I'd check:
- PV input voltage — is it within the right range for your panel setup? Too high and the controller protects itself
- Battery voltage readings — does what VictronConnect shows match a multimeter directly on the terminals?
- MC4 connectors and cable joints — wiggle them while watching the app, see if the numbers jump
- Firmware — connect via VictronConnect and check it's up to date, there were some known bugs in older versions
The 75/15 units are pretty robust in my experience. Mine's been running for three years now with zero issues since I sorted the connector. Victron's not infallible but they're not fragile either.
What does VictronConnect actually show when it's misbehaving? Is it dropping into float prematurely, throwing error codes, or just showing daft numbers? And what panels are you running — any chance the open-circuit voltage is pushing close to the 75V limit in cold weather?
More details would help narrow it down. Others on here will have seen most failure modes at this point so worth describing exactly what the display or app is telling you.