Had a similar head-scratcher last year when I was setting up the emergency backup system in my motorhome. Fitted a Victron isolation transformer to separate the shore power earth from my onboard system — sensible precaution, or so I thought — and immediately had the GFCI on the hookup post tripping every time I connected.
Took me a good few evenings to work it out. The issue was that my transformer secondary was floating (as it should be), but I'd accidentally bonded neutral to earth after the transformer, which confused the GFCI into thinking there was a fault current. Once I removed that bond, everything settled down.
A few things worth checking if you're in a similar situation:
- Is your secondary neutral bonded to earth anywhere downstream? It shouldn't be with an isolation transformer in the circuit
- Check for any stray leakage paths — even a dodgy appliance plugged into the secondary can cause enough imbalance to trip a sensitive GFCI
- Victron's own documentation on isolation transformers is actually quite thorough on this — worth a proper read rather than a skim
I imagine this kind of thing comes up on boat installs quite a bit too, where you've got multiple transformer banks and shore power splits getting complicated fast.
Anyone else navigated this with a multi-transformer setup? Curious whether splitting across separate breaker banks introduces its own complications — feels like the kind of thing that could get messy quickly if the earthing isn't sorted from the start.