Had something similar happen with my cabin setup last spring and it proper stumped me for a while.
I'm running a bank of Fogstar Drift 100Ah cells — four of them in parallel — hooked up to a Victron SmartSolar and a Phoenix charger. Everything was ticking along nicely until I noticed the batteries were barely pulling any current the moment the charger transitioned into absorption. Looked almost like they were full, but the resting voltage told a different story.
Took me a good week of head-scratching before I figured out what was going on. A couple of the batteries were slightly out of balance with each other — one BMS was tripping early and essentially dragging the others with it. Because they're non-communicating units, the Victron had no idea; it just saw voltage climb and backed off like it's supposed to.
A few things worth checking if you're in the same boat:
- Are all your parallel batteries genuinely matched in age and cycle count? Mixing older and newer cells is a recipe for this.
- What absorption voltage are you actually set to? Lithium is far less tolerant of sloppy settings than AGM.
- Have you tried isolating each battery individually and running a slow charge to see if one BMS is the culprit?
The Victron smart lithium preset is a decent starting point but it's not magic — it still needs the underlying batteries to play nicely together.
Anyone else found a more systematic way to diagnose this across a parallel bank without Bluetooth-capable BMS units? Curious whether a simple clamp meter on each feed cable is the way to go.