Interesting one this — I ran into almost exactly the same scenario on my boat build last year, trying to use the load terminals on a Victron 100/30 to top up a secondary device only when the house bank was sitting happy.
The thing worth understanding is that the load output on these controllers isn't really designed as a "overflow charger" — it's primarily meant for DC loads you want to protect from over-discharge. That said, you can absolutely repurpose it for what you're describing, but the devil's in the configuration.
On the Victron, the load output behaviour is set via the BatteryLife algorithm or you can override it with a fixed voltage threshold using VictronConnect. For a LiFePO4 bank, I'd suggest:
- Load on voltage: ~27.0V (for 24V) or ~13.5V (12V)
- Load off voltage: something sensible like 13.0V so you're not hammering the cells
The challenge with feeding something like a Bluetti is that they have their own charge management internally, so you're essentially just providing a DC source — which should be fine, but check what input voltage range your specific Bluetti accepts.
One gotcha I discovered: the load output on the 100/30 is limited to 30A continuous, and depending on how the Bluetti draws power during its own CC/CV cycle, you might see some odd behaviour if it's pulling hard.
Has anyone here actually done this with a Bluetti specifically? Curious whether the input negotiation causes any headaches with a basic MPPT load terminal rather than a proper charger output. My gut says it'll work fine but I'd love to hear real-world experience.