Had a similar headache last year on the boat. Running a pair of Multiplus II 48/5000s through a Cerbo GX, and when my Lynx Shunt started playing up after a saltwater ingress incident, the whole current measurement picture went completely sideways.
The Cerbo was reporting SOC figures that made no sense — showing 80% whilst the batteries were clearly struggling under load. The Fogstar Drift cells I'm running deserve better than that kind of guesswork, especially when I'm also trying to manage EV charging from the system at the cabin.
What I eventually traced it to was the shunt's calibration having drifted rather than a full failure. Victron's support suggested doing a full synchronisation after replacing the unit, but the key thing nobody mentioned upfront was that all three phases need to be stable and balanced at the point of sync, otherwise you're just baking the error in permanently.
A few things worth checking if you're in a similar situation:
- Is the VE.Direct connection between the shunt and Cerbo solid? Mine had developed intermittent dropouts I'd missed
- Have you tried forcing a manual SOC sync via the Cerbo touchscreen?
- Check whether your ESS assistant settings are fighting the shunt readings — mine were, which masked the real problem for weeks
Curious whether anyone else running multiple Multiplus units on a single Lynx bus has seen measurement drift rather than outright failure. Feels like it's more common than Victron's documentation suggests, particularly in marine environments with vibration and humidity thrown into the mix.