Been running a similar setup on my narrowboat for about eight months now — Multiplus 48/5000 paired with a Fogstar Drift 48V bank, so not identical but close enough that this topic grabbed my attention.
The 110A charge current figure on the 48/8000 is the AC-side input limit, not what actually hits the battery terminals. Once you factor in efficiency losses and the inverter/charger's internal topology, real battery-side charge current can differ noticeably depending on your configured absorption voltage and any DVCC limits you've pushed through Cerbo.
A few things worth checking if you're seeing unexpected behaviour:
- DVCC current limit in VenusOS — this is what actually caps battery charge current system-wide when everything's talking properly via CAN-bus
- Your BMS charge current limit (CCL) — is it broadcasting correctly? Use the VRM portal diagnostics or a direct SSH session to confirm the Multiplus is receiving that figure
- AC input current limiter set via VEConfigure — this throttles the whole unit upstream
On my setup I initially had a mismatch between what the BMS was advertising and what Victron was accepting, which led to occasional nuisance alarms without any real fault condition.
Worth also confirming your cable sizing between the Multiplus and battery. At 48V, 110A is still significant — I'd want properly rated busbars rather than relying on the existing loom if you're doing ESS with overnight grid top-up regularly.
Interested whether others running larger 48V LiFePO4 banks in ESS mode have found DVCC actually reliable for current limiting, or whether they've had to add external constraints. My experience has been broadly positive but I suspect boat installations are simpler than