Seeing a few threads lately about hot terminals and I've had a similar scare on the boat that might be worth discussing.
Running a Victron MultiPlus 12/1200 off a Fogstar 100Ah (smaller setup than some of you) and noticed the positive terminal on the inverter getting uncomfortably warm after running the kettle for any length of time. Not melting-anything warm, but warm enough to make me investigate properly.
Turned out to be a combination of things:
- Cable undersized for the actual load — I'd followed a basic guide but hadn't accounted for cable length properly
- Terminal connection not tight enough — resistance at the joint was generating heat
- No busbar — I was running cables directly to the battery terminal which was causing a bit of a rats nest situation
Once I upsized to 70mm² cable, added a proper busbar, and torqued everything correctly with a torque wrench it made a significant difference.
The fuse melting detail in the OP's situation is the bit that concerns me though — is that the ANL fuse or the blade fuse inside the inverter itself? Because if it's the ANL, that's usually a sign the cable or connection upstream is the culprit rather than the fuse rating being wrong.
Has anyone else found that Victron's recommended cable specs in their documentation are more of a minimum rather than a proper working figure for sustained loads? I've been wondering whether they're calculating for short bursts rather than, say, 2–3 minutes of a 700W microwave continuously.
What cable cross-sections are people actually running to their inverters on narrowboats/motorhomes?