Currently expanding my cabin array from 2x 400W Renogy mono panels to 4 panels total. The problem is the 400W panels are discontinued so I've sourced 2x 350W units from a different batch — slightly different Voc (48.3V vs 46.1V) and different Isc too (10.2A vs 9.8A).
My current Victron SmartSolar 100/30 is handling the 2-panel series string fine. If I add the mismatched pair in series and wire both strings in parallel to the same MPPT, the lower-current panels will drag down the whole array at the MPP. I've done the napkin maths and reckon I'm leaving maybe 15-20W on the table constantly, which over a UK summer day probably adds up more than it sounds.
The alternative is picking up a second SmartSolar — maybe a 75/15 just for the smaller string — and keeping them completely independent. That's roughly £80-90 for a new controller vs accepting the derating. On a cabin with a fairly modest load (lighting, router, small 12V fridge), the lost power probably won't kill me, but it feels wrong to deliberately mismatch.
Has anyone actually measured the real-world loss on a mixed parallel string like this, or is the separate MPPT route always the cleaner answer? Wondering if the VRM data from anyone running a similar setup tells a different story to the theory.