Bit of a niche one this, but I've run into something similar on my narrowboat setup and I know a few van builders here have too.
Running a Victron Battery Protect as a virtual load output from a SmartSolar MPPT — great in theory for unattended systems. The MPPT controls the BP via VE.Direct, BP sits between the battery and the load bus, job done. Except...
The MOSFET leakage from the BP when it's supposedly "off" is enough to ghost-trigger the remote L pin on an Orion-Tr Isolated DC-DC converter. We're talking maybe 1-2V of leakage, which shouldn't be enough, but apparently is on some units. My Orion kept waking up intermittently overnight when the BP was commanded off. Took me ages to figure out what was happening.
My workaround was adding a small bleed resistor to pull the remote line properly to ground when the BP cuts out. Crude but it works. Seen others suggest an intermediate relay instead, which is cleaner but adds complexity.
Few questions for the collective:
- Anyone else seen this with newer BP firmware? Wondering if Victron have tightened it up
- Does the non-isolated Orion behave differently here? I'd expect the remote input threshold to be similar but not sure
- For those running unattended installs (holiday let, remote cabin, that sort of thing) — do you just accept the relay approach as best practice?
Would be especially curious to hear from anyone running Fogstar lithium banks with this config — wondering if the BMS cutoff interacts with this leakage issue at all.