Had something similar crop up on my boat last winter — Victron MPPT 150/100 just sitting there showing "off" with no obvious reason. Drove me mad for a couple of days.
In my case it turned out to be a PV voltage issue after I'd reconfigured the array. Worth checking a few things:
Immediate checks:
- What's your actual PV open-circuit voltage reading? With 3 panels in series you could be pushing close to or over the 150V limit depending on temperature — cold mornings can spike Voc significantly higher than the panel spec suggests
- Is the battery voltage showing correctly in VictronConnect or on the Colour Control?
- Any error codes showing? Even a brief flash before it goes "off"
On the EasySolar specifically — I've seen the internal MPPT sometimes need a full power-down reset. Disconnect PV first, then battery, wait a couple of minutes, reconnect battery first, then PV.
Also worth checking whether the MPPT is being remotely controlled via the Colour Control GX — there's a setting that can put it in "off" mode if it's receiving a signal it doesn't like, particularly around grid/generator management even in off-grid setups. Check under Device List > your MPPT > Switch in the GX menu.
What panels are you running and how are they wired — series, parallel or a combination? That'll help figure out if the voltage ceiling is the culprit.
Others on here have had Fogstar or Renogy battery comms interfere with Victron kit too, so if you've added any new components recently that's worth flagging.