Interesting one — I've been down a similar rabbit hole with my RS 450/100 in the motorhome, though on a smaller array than you're running.
The #27 error (short circuit detected) on the RS series is worth investigating carefully before assuming it's a genuine fault. A few things worth checking:
String voltage at the controller input
With 6 panels in series on 650W modules, you'll want to verify your open-circuit Voc doesn't creep too close to the 450V ceiling on a cold morning. UK winters can drop ambient temps enough to push Voc noticeably higher than the STC rated figure. Worth doing the temperature-corrected calculation properly.
Intermittent wiring issues
In my experience, intermittent #27 errors on Victron MPPT RS units are often down to a dodgy MC4 connection rather than an actual short. Any marginal connection can cause the controller to see an unexpected voltage spike or drop and throw the error defensively. I'd go through every MC4 joint on each string methodically — I use a proper MC4 assembly tool (the Amphenol one) and I've found loose crimp connections more than once.
String isolation testing
If you have a decent insulation tester, do a string-by-string check to rule out a panel with degraded insulation to frame. A single damp junction box can cause exactly this kind of intermittent behaviour, especially if you're parked somewhere exposed.
Has anyone else on here dealt with #27 errors specifically on the larger RS units? Curious whether Victron Connect logs are giving you anything useful in the history tab — that's often where I start before touching anything physical.