Had a similar head-scratcher with my Multiplus a while back — green mains LED, bulk charging showing, inverter running, but the low battery red was lit simultaneously. Felt completely contradictory at first.
Turns out the issue was voltage drop under load. The Multiplus reads battery voltage at its own terminals, not at your busbar or distribution point. If your cable runs are even slightly undersized or your connections have any resistance, you'll see a "healthy" reading at the Link 1000 but the Multiplus is actually seeing something lower — especially once it starts pulling current.
A few things worth checking:
- Cable sizing — 12V/3000W setup needs serious cable. Most people underestimate it. You want 70mm² minimum, ideally 95mm²
- Connection quality — one dodgy lug can cause enough resistance to trigger low battery protection under load
- Battery state — if it's a lead-acid bank, surface charge can read 12V at rest but sag badly under any draw
- VE.Configure settings — your low battery cutoff and restart thresholds might just be set too conservatively
I run a Fogstar Drift lithium now and this kind of ghost reading basically disappeared once I sorted the cabling properly. With lead-acid I was constantly chasing weird voltage readings.
Worth connecting a laptop with VE.Configure and watching the actual voltage the Multiplus is seeing in real time rather than trusting a separate meter reading. That'll tell you exactly what's going on.
Anyone else had this on a 12V system specifically? Curious whether it's more common at 12V due to the higher currents involved.